kide
Well-known member
- Joined
- Aug 27, 2006
- Messages
- 3,779
- displayname
- Gerry Ide
Sunny Florida has turned cool...36 degrees this morning. Next door neighbors asked me yesterday to check the odor coming form their fusebox. The A/C breaker was warm, the buss bar was hotter. 50 amp 220 breaker and it stunk (hot phenolic/bakelite). I used an amprobe, showed 44 amps one side, 43 on the other with the heat strip in the A/C heating. I thought that was pretty close to the breaker rating and this was a 20+ year old breaker and suggested replacing it. Then I went out to the A/C and checked the breaker there - it was a 60 amp. Looking at the wire, it was 4AWG stranded copper. Wire good for 70 amps in a 2 conductor config (220 volt, with ground). I replaced the in house breaker with a 60 amp. Why the A/C guy/electrician would feed a 60 Amp with a 50 amp is my head scratcher, as that would turn the 60 amp onr into basically a disconnect switch.